Question

Hey guys,
Just looking for a quick answer to a question: What is the max current that should be run over a 4 guage power wire (16 ft) and what is the largest AGU (cylinder) fuse size that could (should) be used on such a wire. I heard somewhere that the max current should be limited to something like around 130amps, is this right? Thanks,

Fabiano.
Fabe is offline  
Old 06-11-2004, 12:22 PM
  #2  
Merry Christmass from CCA
iTrader: (2)
 
Sassmaster's Avatar
 
Join Date: May 2002
Posts: 2,579
Post

*drags out canadian electrical codebook*

4 guage, 75 degree C rated conductor, 125 amps.
however... since it runs through the engine compartment, which can get pretty warm, we have to derate the cable somewhat, I'm using 40 degrees C as an ambient temperature just for the sake of arguement, which gives us a derating factor of .88

so, 125 amps, X .88 = 110 amps.

why did I do this? generally, I find that the codebook is a great guideline for setting fuse/conductor sizes
Sassmaster is offline  
Old 06-11-2004, 06:10 PM
  #3  
0 Watt CAFz'r
 
JTerp's Avatar
 
Join Date: Jun 2004
Posts: 8
Post

Good guy to keep around.

I think I'll be looking around for one of those books now.
JTerp is offline  
Old 06-11-2004, 06:46 PM
  #4  
50 Watt CAFz'r
Thread Starter
 
Fabe's Avatar
 
Join Date: Apr 2004
Posts: 194
Post

So basically I suck because I will soon be having 210 amps and a 4 guage that's going to spontaneously combust! Thanks guys, let the inferno begin...
Fabe is offline  
Old 06-11-2004, 06:51 PM
  #5  
0 Watt CAFz'r
 
JTerp's Avatar
 
Join Date: Jun 2004
Posts: 8
Post

I've done most of my own training by trial and error. I've also made lots of smoke appear from behind my dash when I was growing up. PS: Never use 22awg wire for power wire.

Something I should ask is: What equipment are you using to get 210 amps of draw.

[ June 11, 2004, 08:13 PM: Message edited by: JTerp ]
JTerp is offline  
Old 06-11-2004, 11:36 PM
  #7  
4000 Watt CAFz'r
iTrader: (19)
 
2 8's AKA Jeepbeats's Avatar
 
Join Date: May 2001
Posts: 5,644
Post

Originally posted by Sassmaster:
*drags out canadian electrical codebook*

4 guage, 75 degree C rated conductor, 125 amps.
however... since it runs through the engine compartment, which can get pretty warm, we have to derate the cable somewhat, I'm using 40 degrees C as an ambient temperature just for the sake of arguement, which gives us a derating factor of .88

so, 125 amps, X .88 = 110 amps.

why did I do this? generally, I find that the codebook is a great guideline for setting fuse/conductor sizes
Just curious, the code book is for solid wire right, or does it apply the same way to multistrand wire? It goes by cirular mils, or something along those lines?
2 8's AKA Jeepbeats is offline  
Old 06-12-2004, 04:33 AM
  #8  
Merry Christmass from CCA
iTrader: (2)
 
Sassmaster's Avatar
 
Join Date: May 2002
Posts: 2,579
Post

it goes by the wire guage, which is based on circular mils, not the physical size. a 1/0 solid wire is physically smaller than a 1/0 19 strand wire, but 1/0 welding cable is in between.
Sassmaster is offline  
Old 06-12-2004, 04:58 AM
  #9  
Tzu
50 Watt CAFz'r
iTrader: (1)
 
Tzu's Avatar
 
Join Date: Nov 2003
Posts: 376
Post

this should help you out

http://www.the12volt.com/info/recwirsz.asp
Tzu is offline  
Old 06-12-2004, 08:04 AM
  #10  
4000 Watt CAFz'r
iTrader: (19)
 
2 8's AKA Jeepbeats's Avatar
 
Join Date: May 2001
Posts: 5,644
Post

Thanks guys!
2 8's AKA Jeepbeats is offline  


Quick Reply: Max power for wire size and fuse question



All times are GMT -5. The time now is 07:35 AM.